Common Earth or Seperate

Topics about the Hardware of Revolution Pi
Post Reply
h2oil
Posts: 10
Joined: 17 Jan 2020, 17:30
Answers: 0

Common Earth or Seperate

Post by h2oil »

Is it ok to Earth the AIO module along with the RevPi Connect on same earth as a 220-24VDC transformer?

Just want to check no signal noise for mA reading will be made

Thanks :)
User avatar
dirk
KUNBUS
Posts: 1948
Joined: 15 Dec 2016, 13:19
Answers: 4

Re: Common Earth or Seperate

Post by dirk »

Hi h2oil, this is a question that I have to ask in the hardware department.
User avatar
dirk
KUNBUS
Posts: 1948
Joined: 15 Dec 2016, 13:19
Answers: 4

Re: Common Earth or Seperate

Post by dirk »

Hi, to make it short - you can use a common ground for the AIO and your power supply. It depends on your measuerement accuracy requirements. In case you want mV accuracy the line resistance i.e. may be involved here.
Post Reply